[mrtg] Reporting incorect values
John Mulkerin
jmulkerin at comcast.net
Mon Jan 3 03:41:01 MET 2005
Trying to monitor a Powerware UPS Battery Load
When I do an snmpget for 1.3.6.1.4.1.534.1.4.1.0 I get an integer of 27 but
my MRTG grapgh and log says 100. I know 27% is the right answer so why
does mrtg report 100? I've read and reread the mrtg refence pages. What
am I doing wrong?
Target[UPS_6]: 1.3.6.1.4.1.534.1.4.1.0:public at 10.10.2.4:
YLegend[UPS_6]: Battery Load
ShortLegend[UPS_6]: %
MaxBytes[UPS_6]: 100
Options[UPS_6]: growright,nopercent, gauge, unknaszero
Unscaled[UPS_6]: dwmy
Legend1[UPS_6]: Battery Load
Legend2[UPS_6]: .
Legend3[UPS_6]: Max value per interval on graph
Legend4[UPS_6]: .
LegendI[UPS_6]: Load:
LegendO[UPS_6]: .
Title[UPS_6]: UPS Load
PageTop[UPS_6]: <H1>Computer Room UPS Load</H1>
Colours[UPS_6]: GREEN#00eb0c,BLUE#0000ff,GRAY#AAAAAA,VIOLET#ff00ff
WithPeak[UPS_6]: ymw