On Fri, 2007-06-08 at 07:36 -0500, Scott Danton wrote:
> I have recently purchased a Room Alert 7E to monitor the temperature
> of our Server room.  I am wondering if anyone has any experience
> monitoring the temperature from a Room Alert device with MRTG? 

No, but a plethora of other temperature sensors (my current favorite:
Itwatchdogs Weathergoose)

>  I would love to get some help on a config.  Looking at the
> documentation they have built in MIB for Temp1F and Temp2F for the
> temperature settings.  I am not sure how to use these.  I know for
> monitoring a network interface in MRTG you would use something like
> 172.16.2.10_2 Do I use the same thought process and do
> 172.16.2.10_Temp1F? 

The name is mostly irrelevant.  The target is everything.

>  How do I set up the graph for temperature?  As you might be able to
> tell I am not real sure of what I am doing.  Please send anything you
> think will be helpful. Even a sample cfg file if you have one.

Here's a sample.  To make this work, I used a LoadMIBs: line that
included the mib file (and any pre-requisite mibs)

# Created by 
# /usr/bin/cfgmaker --ifref=name --nointerfaces
--host-template=probe.template --subdir=central/HOSTNAME
--output=/var/mrtg/cfg/central/foo-probe.cfg
public at foo-probe.example.com::2:1:1:1


### Global Config Options

#  for UNIX
# WorkDir: /home/http/mrtg

#  or for NT
# WorkDir: c:\mrtgdata

### Global Defaults

#  to get bits instead of bytes and graphs growing to the right
# Options[_]: growright, bits

EnableIPv6: no

######################################################################
# System: foo-probe
# Description: SH2 (3.5)
# Contact: Dan McDonald 
# Location: foo Substation
######################################################################
#.....................................................................
Target[foo-probe.example.com.temp.1]:
SH2SensorCurrentValue.1&SH2SensorCurrentValue.1:public at foo-probe.example.com
bb*host[foo-probe.example.com.temp.1]: foo-probe.example.com
bb*svc[foo-probe.example.com.temp.1]: temp
bb*yellow[foo-probe.example.com.temp.1]: 83
bb*red[foo-probe.example.com.temp.1]: 88
routers.cgi*Options[foo-probe.example.com.temp.1]: nototal
Directory[foo-probe.example.com.temp.1]: central/foo-probe.example.com
MaxBytes[foo-probe.example.com.temp.1]: 185
RouterUptime[foo-probe.example.com.temp.1]: public at foo-probe.example.com
Options[foo-probe.example.com.temp.1]: Gauge noi
Title[foo-probe.example.com.temp.1]: Probe temperature gauge
YLegend[foo-probe.example.com.temp.1]: degrees F
ShortLegend[foo-probe.example.com.temp.1]: F
PageTop[foo-probe.example.com.temp.1]: <H1>Temperature</H1>
 <TABLE>
   <TR><TD>System:</TD><TD>foo-probe  </TD></TR>
   <TR><TD>Location:</TD><TD>foo Substation </TD></TR>
 </TABLE>
Target[foo-probe.example.com.hum.2]:
SH2SensorCurrentValue.2&SH2SensorCurrentValue.2:public at foo-probe.example.com
bb*host[foo-probe.example.com.hum.2]: foo-probe.example.com
bb*svc[foo-probe.example.com.hum.2]: humidity
bb*yellow[foo-probe.example.com.hum.2]: 17:80
bb*red[foo-probe.example.com.hum.2]: 12:85
routers.cgi*Options[foo-probe.example.com.hum.2]: nototal
Directory[foo-probe.example.com.hum.2]: central/foo-probe.example.com
MaxBytes[foo-probe.example.com.hum.2]: 100
RouterUptime[foo-probe.example.com.hum.2]: public at foo-probe.example.com
Options[foo-probe.example.com.hum.2]: Gauge noi
Title[foo-probe.example.com.hum.2]: Probe humidity gauge
YLegend[foo-probe.example.com.hum.2]: relative humidity
ShortLegend[foo-probe.example.com.hum.2]: %
PageTop[foo-probe.example.com.hum.2]: <H1>Humidity</H1>
 <TABLE>
   <TR><TD>System:</TD><TD>foo-probe  </TD></TR>
   <TR><TD>Location:</TD><TD>foo Substation </TD></TR>
 </TABLE>




> 
-- 
Daniel J McDonald, CCIE # 2495, CISSP # 78281, CNX
Austin Energy
http://www.austinenergy.com