Gauge was it - Thank you Paul. I should have seen that coming - I knew it
already. Sorry. Hope this helps others as well....
-----Original Message-----
From: Paul C. Williamson [mailto:pwilliamson at mandtbank.com]
Sent: Tuesday, December 11, 2001 3:31 PM
To: Chirhart, Brian
Cc: MRTG#032#users#032##060#mrtg at list.ee.ethz.ch#062#
Subject: RE: [mrtg] APC UPS Powernet Web management card
Changing from the OID to the MIB only adds complexity. Only go to
there once the OID is working properly. There's really no technical
reason to use it. Just easier on readability of the config. It actually
adds overhead because you need to load the MIB in order to
run the query.
As for gauge, that is most likely it. The best way to determine that
is to look at the log file. If the first line is populated and all the
rest are zeros, it indicates you should probably use gauge (if it
works from the command line).
Paul
>>> "Chirhart, Brian" <bchirhart at fnni.com> 12/11/01 03:22PM >>>
Currently I use just the Oid, but I was going to try the MIB since it was
not working.
As for Guage - only on the Load section - could that be it?
-----Original Message-----
From: Paul C. Williamson [mailto:pwilliamson at mandtbank.com]
Sent: Tuesday, December 11, 2001 2:21 PM
To: Chirhart, Brian; mrtg at list.ee.ethz.ch
Subject: Re: [mrtg] APC UPS Powernet Web management card
If you use MRTG, do you use gauge?
As for loadMIBs, why are you doing that? Do you use the
MIB in the target line or the OID?
Paul
>>> "Chirhart, Brian" <bchirhart at fnni.com> 12/11/01 03:10PM >>>
> Hello everyone -
>
> I have a lot of Oid's for APC UPS devices, but when I try to graph them
> using MRTG or STG I get flatlines, but if I try a MIB Browser, like GetIF,
> I can get the values and graph them. Any ideas why I wouldn't be able to
> do it in MRTG?
>
> For example:
> Battery Capacity - 1.3.6.1.4.1.318.1.1.1.2.2.1.0
> Temperature - 1.3.6.1.4.1.318.1.1.1.2.2.2.0
> Input Voltage - 1.3.6.1.4.1.318.1.1.1.3.2.1.0
> Frequency - 1.3.6.1.4.1.318.1.1.1.3.2.4.0
>
> The crazy thing is that I CAN get Load which is:
> 1.3.6.1.4.1.318.1.1.1.4.2.3.0
>
> Also - when using the LoadMIBs line do I want to specify a specific MIB or
> just the directory it resides in?
>
> Thx -
> Brian
--